What infinity said but assuming it's a 3 phase panel I'm hoping it could handle more than 3 circuits. Otherwise, why are you installing one? On a related note, if you can only max at 2 circuits, you're going to be having problems because that means that one of the phases is overloaded.
Too much load, of course.How would one of the phases be overloaded ?
How would one of the phases be overloaded ?
Too much load, of course.
The thing not mentioned in OP is how much load is on each circuit.
If you have a 30A 3-phasee sub-panel and it is fully loaded after 2 circuits, I don't know how that is possible without one phase having more than 30A on it.
Fully loaded and Overloaded are two different scenarios.
I've seen a 42-circuit panel fed from a 50A breaker... all depends what the loads are.Is there a max number of circuits that can be fed from a 30A sub panel? I'm thinking a max of 2 circuits. Is thera a limit per code?
Is there a max number of circuits that can be fed from a 30A sub panel? I'm thinking a max of 2 circuits. Is thera a limit per code?
It's a single phase 120/240 4 wire sub panel feeding enterance lights to mobile home park. 1 20A 120V circuit for lights and another 20A 120V circuit for sump pump. I would like to add another 120V circuit for high water alarm.
Go for it..... I would like to add another 120V circuit for high water alarm.