This might follow Charlie's statement on the reason's we might wan't to make a proposal.
And this one it has been a thorn sometimes with allot of inspectors and contractors. as we have seen post here already.
1.) NEC Section/Paragraph: 310.15(B)(2) add Exception 6.
2.) Proposal Recommends: [new text]
(Exception No. 6: derating factors shall not apply to cables ran in bored holes, or cut notches in floor joist or interior walls in residential dwellings where it meets
(a) Where these cables are run in bored holes in a wall, Floor, or ceiling space,where the ambient temperature will not exceed 40 deg. C. in normal use.
(b) Where these cables are run in any floor, wall or ceiling space with a high ambient temperature, The derating require in 310.15(B)(2) shall be followed.
4.) Substantiation: Where there is cables ran in bored holes in joist with spacing between each joist, the maximum load on these cables, will most likely never be used. the temperature of these cables would never run beyond the safely rated temperature of the cable. As the code is now it requires multiple holes to be bored in floor joist to accommodate the circuit runs and most building regulations limit the amount of these holes that can be safely bored into floor joist.
So very true. But sometimes there are some unnecessary codes that conflict with other building codes that can make an installation more complicated than it needs to be.From another thread by Charlie: A lot of proposals are generated by individuals who are trying to get relief from a particular inspector or group of inspectors.
And this one it has been a thorn sometimes with allot of inspectors and contractors. as we have seen post here already.
1.) NEC Section/Paragraph: 310.15(B)(2) add Exception 6.
2.) Proposal Recommends: [new text]
(Exception No. 6: derating factors shall not apply to cables ran in bored holes, or cut notches in floor joist or interior walls in residential dwellings where it meets
(a) Where these cables are run in bored holes in a wall, Floor, or ceiling space,where the ambient temperature will not exceed 40 deg. C. in normal use.
(b) Where these cables are run in any floor, wall or ceiling space with a high ambient temperature, The derating require in 310.15(B)(2) shall be followed.
4.) Substantiation: Where there is cables ran in bored holes in joist with spacing between each joist, the maximum load on these cables, will most likely never be used. the temperature of these cables would never run beyond the safely rated temperature of the cable. As the code is now it requires multiple holes to be bored in floor joist to accommodate the circuit runs and most building regulations limit the amount of these holes that can be safely bored into floor joist.