Re: 310.15(B)(2) add Exception 6.
First is the following text what will be submitted?
I ask because IMO this proposed exception is very similar to an exception near and dear to me and there is no mention of ambient temps in it.
IMO 310.15(B)(2) is already a convoluted article, the addition of yet another exception will exasperate that.
Here is what I imagine, my changes in bold.
This is not so easy.
What do you all think?
Wayne I hope you understand that I am not criticizing your efforts, I think you have a great idea.
Good luck to you with this.
Bob
I also think this is a great idea, and would like to make few comments.Originally posted by charlie:
I like the concept and have made some suggested changes. We are ready for more comments and tweaking.
First is the following text what will be submitted?
Why did "and where the ambient temperature will not exceed 30?C in normal use." get added?1.) NEC Section/Paragraph: 310.15(B)(2) add Exception 6.
2.) Proposal Recommends: [new text]
Exception No. 6: derating factors shall not apply to cables ran in bored holes, or cut notches in joists or interior walls in dwellings under the following conditions:
(1) Where these cables are run in bored holes in a wall, floor, or ceiling space, and where the ambient temperature will not exceed 30?C in normal use.
(2) Not more than 10 current carrying conductors are included in the bundle and are not larger that No. 12 Cu. or No. 10 Al.
4.) Substantiation: Where there are cables run in bored holes in joists with spacing between each joist, the maximum load on these cables, will most likely never be used because of the load profiles in dwelling units. The temperature rise of these cables is minimal under these conditions. By limiting this exception to 15 and 20 ampere circuits, the range, dryer, electric furnace, etc. are excluded and the likelihood of more than one or two heavily loaded circuits are eliminated.
The code now requires multiple holes to be bored in floor joists to accommodate the runs and building regulations limit the amount of these holes that can be safely bored into floor joist. This places an undue burden on the electrician to find exit routing from panelboards. This proposal will provide some relief from the stringent requirements.
I ask because IMO this proposed exception is very similar to an exception near and dear to me and there is no mention of ambient temps in it.
I feel the proposal could simply ask for the addition of NM and tweaking to this existing exception.310.15(B)(2)Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(a)Each cable has not more than three current-carrying conductors.
(b)The conductors are 12 AWG copper.
(c)Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.
IMO 310.15(B)(2) is already a convoluted article, the addition of yet another exception will exasperate that.
Here is what I imagine, my changes in bold.
I do wonder about my adding 14 AWG to the existing MC requirements?310.15(B)(2)Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket or to Type NM or UF cable under the following conditions:
(a)Each cable has not more than three current-carrying conductors.
(b)The conductors are 12 AWG or 14 AWG copper.
(c)Not more than 20 current-carrying conductors are bundled, stacked, run in bored holes in a wall, floor, or ceiling space or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.
Substantiation: Where there are cables run in bored holes in joists, studs, etc snip, the maximum load on these cables, will most likely never be used because of the load profiles of 15 and 20 amp circuits snip. The temperature rise of these cables is minimal under these conditions. By limiting this exception to 15 and 20 ampere circuits, the range, dryer, electric furnace, etc. are excluded and the likelihood of more than one or two heavily loaded circuits are eliminated.
The code now requires multiple holes to be bored in floor joists to accommodate the runs and building regulations limit the amount of these holes that can be safely bored into floor joist. This places an undue burden on the electrician to find exit routing from panelboards. This proposal will provide some relief from the stringent requirements.
This is not so easy.
What do you all think?
Wayne I hope you understand that I am not criticizing your efforts, I think you have a great idea.
Good luck to you with this.
Bob