Morning George, let start by saying I wish the NEC was more clear about this.......in other words I am not that confident I have the real answer here. :lol:
Nope :?
No we are not OK in the 158 F attic, you can not roll up to the next higher breaker on that 14.5 amp cable if it supplies a multi-outlet circuit suppling receptacles as most dwelling unit circuits are.
Correct just as it is when figuring for ambient temperature.
I have a hard time with that statement.
If I accept what you say than I should also be able to apply this averaging to the actual current I run through the conductor.
Why not run 30 amps through a 14 AWG for 5 minutes an hour the other 55 minutes the load is 2 amps.
I know for a fact the insulation will survive that but it is against the code to do so.
Who are we to second guess the NEC on the Ambient temps?
Bob
georgestolz said:It doesn't. Since you brought it up, I looked closer:iwire said:Where in the NEC tells us we can use the average temperature? :?:
Unfortunately, it doesn't provide much assistance in decision making. :?310.10, FPN No.1, (1) Ambient temperature ? ambient temperature may vary along the conductor length as well as from time to time.
Nope :?
georgestolz said:If so, we're still okay. A 14-2 NM cable in a 140?F attic has an ampacity of 17.25 amps. The same cable in a 158? attic has an ampacity of 14.5 amps. Provided the load does not exceed 14.5 amps for less than three hours, or 11.6 amps for over three hours, then we're still okay.IMO we have to use the maximum expected temperature.
No we are not OK in the 158 F attic, you can not roll up to the next higher breaker on that 14.5 amp cable if it supplies a multi-outlet circuit suppling receptacles as most dwelling unit circuits are.
georgestolz said:Neither. The expected load does not factor into derating, until you have finished the derating process. Once we're done derating, then we can turn our attention back to the load, and overcurrent protection.When derating conductors for fill do you use the highest ampacity a conductor may carry or do you use the average ampacity the conductor may carry?
Correct just as it is when figuring for ambient temperature.
georgestolz said:But the damage isn't a foregone conclusion. I think what's messing with us is that we're trying to determine mathematically if a conductor is going to be damaged under certain conditions. If we assume that the damage is guaranteed, then we would be inclined to follow the "max temperature" approach.To me it is the same issue we are dealing with heat damaging the insulation.
I have a hard time with that statement.
If I accept what you say than I should also be able to apply this averaging to the actual current I run through the conductor.
Why not run 30 amps through a 14 AWG for 5 minutes an hour the other 55 minutes the load is 2 amps.
I know for a fact the insulation will survive that but it is against the code to do so.
Who are we to second guess the NEC on the Ambient temps?
Bob