From what the OP described the 600 kcmil conductors are feeding the meter after the service point so they're not on the POCO side.Now if the service conductors are larger coming from the power company (600 kcm)then, imo, the bond must be based on the larger size conductors, thus 1/0 copper or 3/0 aluminum