See if the helps for determining the load:
230.42 Minimum Size and Rating.
(A) General. The ampacity of service-entrance conductors
shall not be less than either 230.42(A)(1), (A)(2), or (A)(3).
Loads shall be determined in accordance with Part III, IV,
or V of Article 220, as applicable. Ampacity shall be determined
from 310.15. The maximum allowable current of
busways shall be that value for which the busway has been
listed or labeled.
(1) The sum of the noncontinuous loads plus 125 percent
of continuous loads
(2) The sum of the noncontinuous load plus the continuous
load after the application of any adjustment or correction
factors.
(3) The sum of the noncontinuous load plus the continuous
load if the service-entrance conductors terminate in an
overcurrent device where both the overcurrent device
and its assembly are listed for operation at 100 percent
of their rating