Non continuous loads add up to 400A
Continuous loads add up to 320A
Combo example: 200A non continuous plus 160A continuous (multiply 160 x 1.25 = 200A) = 400A Service.
Apply the rules to the 320(400) meter base.
Thanks for clarifying. And that is just as I thought.
It would really help if we stopped calling it 320 and call it 400 because it is as much a 400 as a 400 amp panel is.
I agree completely. To me, it would make the most sense if every power distribution product were rated on the same standard of ampacity, with a common calculation from the loads, no matter what kind of equipment it is.
Anything else seems like the thought process of, "we'll raise the speed limits 25%, but we will also make the speedometers falsely display 125% of the speed".
There is another issue, that I've seen discussed regarding 320 meterbases. It is common that they may only have a single terminal per phase. In the 400A realm, I commonly see parallel sets strategically specified. So if you plan on doing this, be aware that the meterbase may not be able to directly connect to such a feeder, and could need the equivalent single set instead.