320amp vs 400amp

Status
Not open for further replies.

jumper

Senior Member
From what I've been told. It is technically a 320A meter socket, but people install 2 - 200A panels off of it all the time...resulting in the "400A" name. Not saying that is correct, just passing along the information. Also...I am still an apprentice...so there's that... :blink:

Hang tight, maybe we can explain this to you.

Welcome to the forum.
 

Carultch

Senior Member
Location
Massachusetts
I am not. I am trying to answer.

If I am unclear I can try and explain differently.

I'm trying to ask how to add up non-continuous loads, when using a 320A meter socket. Do non-continuous loads add up to 320A? Or do non-continuous loads add up to 400A?

It is my understanding that continuous loads, when using a 320A meter socket, can add up to 320A, and then multiply by 125% to determine the 400A breaker and 400A service. I also understand that most serviceequipment is in general, sized by 100% non-continuous plus 125% continuous. Please correct me if I am wrong.

In otherwords, is 320A "continuous duty" rated equipment suitable for all applications where a 400A standard OCPD would be used?
 
Last edited:

iwire

Moderator
Staff member
Location
Massachusetts
I'm trying to ask how to add up non-continuous loads, when using a 320A meter socket. Do non-continuous loads add up to 320A? Or do non-continuous loads add up to 400A?


It is my understanding that continuous loads, when using a 320A meter socket, can add up to 320A, and then multiply by 125% to determine the 400A breaker and 400A service. Please correct me if I am wrong.

There is nothing different in sizing a meter socket from a panel or service.

Add all the non-continuos loads up.

Add all the continuos loads up and multiply by 1.25.

Take the result of that multiplication and add it to the first figure, if the resulting sum is 400 amps or less a 320 class meter is fine.
 

jumper

Senior Member
I'm trying to ask how to add up non-continuous loads, when using a 320A meter socket. Do non-continuous loads add up to 320A? Or do non-continuous loads add up to 400A?.

Non continuous loads add up to 400A

Continuous loads add up to 320A

Combo example: 200A non continuous plus 160A continuous (multiply 160 x 1.25 = 200A) = 400A Service.

Apply the rules to the 320(400) meter base.



It is my understanding that continuous loads, when using a 320A meter socket, can add up to 320A, and then multiply by 125% to determine the 400A breaker and 400A service. Please correct me if I am wrong.

Yes. Service conductors would be need to be sized for 400A also.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you performed an Article 220 load calculation and came out with 375 amps to size the service what would you use?
 

Carultch

Senior Member
Location
Massachusetts
Non continuous loads add up to 400A

Continuous loads add up to 320A

Combo example: 200A non continuous plus 160A continuous (multiply 160 x 1.25 = 200A) = 400A Service.

Apply the rules to the 320(400) meter base.

Thanks for clarifying. And that is just as I thought.

It would really help if we stopped calling it 320 and call it 400 because it is as much a 400 as a 400 amp panel is.

I agree completely. To me, it would make the most sense if every power distribution product were rated on the same standard of ampacity, with a common calculation from the loads, no matter what kind of equipment it is.

Anything else seems like the thought process of, "we'll raise the speed limits 25%, but we will also make the speedometers falsely display 125% of the speed".

There is another issue, that I've seen discussed regarding 320 meterbases. It is common that they may only have a single terminal per phase. In the 400A realm, I commonly see parallel sets strategically specified. So if you plan on doing this, be aware that the meterbase may not be able to directly connect to such a feeder, and could need the equivalent single set instead.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
If you performed an Article 220 load calculation and came out with 375 amps to size the service what would you use?
What metering equipment? Whatever the POCO wants me to use, if it is dwelling unit the chance of it being a 320 socket is much greater then for non dwelling application.

Irrelevant and off topic but the poco will still connect that 320/400 amp service to a 25 kva transformer. :p
That happens too.

I have a project coming up where I will be installing 1200 amp 208/120 service disconnecting means. POCO is only going to provide a 225kVA transformer, but actual load calculation is only around 600-700 amps (225 is 625A). If there is ever more load added in future however all that needs changed is the transformer (if demand data warrants it at that time).
 

iwire

Moderator
Staff member
Location
Massachusetts
So I guess I'm Still not understanding the rating you would get if you ct meter a 400 amp service

CTs could be used for any size service, if you need to install CT metering is a choice the power company makes.

Keep in mind direct reading plug in meters are limited to 400 amps, so in many areas any service more than 400 amps is gong to get CTs.
 