I posted a meter/main that has a continuous 320 amp rating for the equipment -- - All service calulations are a continuous load and non continuous load --
Right, that is the key the continuous load portion has already been increased by 25%
So as a quick example, a large home is heated with electric. That must be treated as a continuous load per the NEC.
Lets say you add up all the heat and it comes out to 200 amps
Now you have add 25% to that
200x1.25=250 amps
Now all the rest of the loads are non-continuous and add up to a total of 150 amps
250 +150 = 400 amps. This means I can use the class 320 meter socket rated 400 amps max