al hildenbrand
- Minnesota
- Electrical Contractor, Electrical Consultant, Electrical Engineer
I clearly hear you, and understand you.Totally disagree.
I just did.You can't seriously compare the two situations.
7-47 Log #3415 NEC-P07 Final Action: Reject
(334.30)
________
Submitter: Steve Carle, Advanced Currents Corp.
Recommendation: Revise text to read as follows:
334.30 Securing and Supporting.
Nonmetallic-sheathed cable shall be supported and secured by staples, cable
ties, straps, hangers, or similar fittings designed and installed so as to not
damage the cable, at intervals not exceeding 1.4 m (4 ½ ft) and within 300 mm
(12 in.) of every outlet box, junction box, cabinet, or fitting. Flat cables shall
not be stapled on edge.
Sections of cable protected from physical damage by raceway shall not be
required to be secured within the raceway.
(D) Connector Fitting with Incorporated Box.
A connector fitting with incorporated box identified for the use shall be
permitted where the cable is secured in place at intervals not exceeding 1.4 m
(4 ½ ft) and within 300 mm (12 in.) from the connector fitting, and there shall
be at least a 300 mm (12 in.) loop of unbroken cable which allows the
connector fitting to be pulled forward at least 150 mm (6 in.) from its installed
position for field inspection of connections or to permit replacement.
Substantiation: Just like the “Wiring Device Without a Separate Outlet Box”
needs a service loop of wire as described in 334.30 (C), so does this new
methodology defined in companion proposals. This service loop allows for safe
field inspection and serviceability of the connections and devices.
Note: This is a companion proposal to 100, 300.15 and 314.16.
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Reject
Panel Statement: The loop proposed by the submitter is not prohibited in the
current language of this section and 334.30 only requires that the cable be
supported within 12 in. of the outlet box, junction box, cabinet, or fitting.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 14
________________________________________________________________
No, I wouldn't fire you but I would tell you to make sure there isn't more than 12" of cable between the staple and the box. Why? because you will probably fail in some areas around here.
I am sorry but I cannot understand your thinking on this. If you allow this in a ceiling for a can you will have to allow a staple 6" from a switch box with 4' of cable looped. Now there are 3 cables in that box... will you allow all 3 cables with a 4' loop?
thanks for finding and posting that, iwire. Very good of you.![]()
Well I went looking in the ROPs for something to prove my point.Instead I found something that precisely disproved my point. DOH! :ashamed1:
I would have liked to have closed the pdf and forgotten about it but that would not be right.
I'm going to start leaving 10 feet of slack at every box "just in case".![]()
I am not convinced. I do not read that info as allowing more than 12". IMO, it is talking about a box like one sees in a trailer where the receptacle is incorporated as part of the box.
:huh:
The panel statement clearly states you and I were wrong.
Well I guess I am reading it differently.
Yes. You are.
And the Code Making Panel is saying they wrote it NOT your way, but a way that doesn't limit the actual length of the cable, but only limits the distance between the support and the box.
I believe this is the "CMP intent" that people hold so high . . .
See, this is the problem with reading the published words of the Code and saying the Code only means some unpublished "intent", regardless of the actual printed Code words. To paraphrase a famous rule by Charlie B., the Code only says what it says. You have to read it as if for the very first time, . . . it does not say what you were taught it says, it does not say what you want it to say. And, in spite of the CMP's intent to say something else, it only says what it says.I wonder if the original CMP members who drafted the rule in the first place felt the same as the one giving an opinion in and ROP
IMO, if this is not the case I find little reason to require a reduction in the securing requirement to 8 in. or for uniformity the rules should just say within 8 inches.
I agree. And he has stated his municipal rule that is in play, with this:It’s up to the OP who seems to represent the Authority to clarify this with his authority
Our municipal rule is that the code must be very specific and admissible in court. In other words, the "neat and workmanlike manner" is a subjective rule and not enforceable.