376.22 metal wireway

Status
Not open for further replies.
Buck

Seems to me that is the intent of 376.22(B), but the language could have been more specific

Brian
 
buck33k said:
I see there has been an 08 change in 376.22 for clarification.

So as an example, 31 CCCs anywhere in the wireway would be adjusted down to 40% ampacity...all 31. Not to exceed 20% cross sectional area. Is this correct?

Correct, any time you exceed 30 CCCs in any cross sectional area of the wireway you must apply the adjustment factors of 310.15(B)(2)(a).

Chris
 