Quite so!Like DC bus capacitors in VFDs, I presume?
Quite so!Like DC bus capacitors in VFDs, I presume?
Passive units???So what do you put in 480 volt units?
So, what are the kind with a start cap and a centrifugal switch (with or without a run cap)?Eddie, a 1ph PSC has one cap inline with the start coil, this cap is that "start" and "run" cap, it's a continuous duty cap. One cap morphs from "start" to "run" because of how the EMF builds up, which reduces the amps from about LRA back down to run amps.
Often we say "start cap" that is a helper cap, it parallels the PSC cap for a brief moment to get a little more phase shift into the start coil, which allows a hard-to-start PSC to start with a bit more start torque, hence using less power at "start" time.
Passive units???
That's cheating.........!Air conditioning unit.
That's a CSCR motor. Will have two caps and the Start one will parallel the Run cap and when the "centrifugal relay" gets enough rpm it will cut out the start cap.So, what are the kind with a start cap and a centrifugal switch (with or without a run cap)?
And what usually happens is that the internal overload opens when the motor does not start, and the time it takes the overload to reset is usually sufficient to allow the restart to be successful. You can also see this happen when you unplug and replug almost any equipment which contains a hermetically sealed compressor, or where you quick cycle the thermostat on a whole house AC....
Ever cycle a window unit thermostat quick and here the compressor hum and not start? That"s because the refrigerant pressure has not equalized yet and the compressor is CSCR can't start with differential pressure. It will start when you wait longer and the pressures equalize.
...
Some residential thermostats have a time delay built in. Some equipment (usually the larger stuff) have TDs built inAnd what usually happens is that the internal overload opens when the motor does not start, and the time it takes the overload to reset is usually sufficient to allow the restart to be successful. You can also see this happen when you unplug and replug almost any equipment which contains a hermetically sealed compressor, or where you quick cycle the thermostat on a whole house AC.
Have you seen equipment which incorporates the delay into the control system?
My heat pump does.\
Have you seen equipment which incorporates the delay into the control system?
On a PSC, the run cap voltage (across the cap terminals, tested with a V meter) when running is usually higher than line voltage. 1.5x line V is what I see most caps rated for.So yes, a 370 VAC cap might be able to used on a 480 VAC motor. Of course a 600 VAC cap would last longer.