Ahhh... the old "I got such a deal on this!" problem. Wasn't such a deal after all now, was it?
380V in other parts of the world is ALWAYS a Wye connection (they call it "Star") connection and it is VERY common to use Phase-to-Neutral as the control voltage, because it is "free". You now have three problems;
380V in other parts of the world is ALWAYS a Wye connection (they call it "Star") connection and it is VERY common to use Phase-to-Neutral as the control voltage, because it is "free". You now have three problems;
- It will not work, and ...
- You are EXCEDING the Ground Reference Voltage of the equipment. It is designed to never see more than 220V to ground. By connecting it to a Delta 380V system, the ground reference is now floating (as evidenced by your different readings, which are more likely capacitive). You can have serious problems with any controls, electronics and protective devices that might be part of this unit. You will need to get them a 380Y220V transformer, and...
- It is almost CERTAINLY not UL listed, so make sure that you, as the EC, cover your butt from a liability standpoint in that you are connecting unlisted equipment, which may be a problem with their insurance carrier if anything should go wrong, and you will want it IN WRITING that you informed them that this is the case.