3P disconnect, 1P output

Status
Not open for further replies.

B2Buckaroo

Member
Location
Minnesota
Occupation
electrician
30a 3 phase disconnect fed from a 208 4w 30a circuit. (2 loads) phases 1 & 3 fused at 30a 208, phase 2 fused at 20a 120v. Allowing operator to lockout both components of a weld station (feeder and power supply) with a single lock. Is this NEC compliant?
 
Is there any code section that would require it to be labeled that it is fed with two different sources of power?
 
The disconnect is fed from a single source ...

I'm assuming you mean a 3-pole breaker.

One could say it's been turned into a mutli-wire branch circuit. And that is fine. If it were fed by separate breakers then it might violate 210.4(C), but by using a 3-pole breaker you qualify for exception 2.

I'm not sure that it's even a violation without the three pole breaker, because I don't see any prohibitions on optional disconnects that open multiple circuits, MWBC or otherwise. I do think the 3-pole breaker is prudent and eliminates ambiguity regarding compliance.
 
So this is a 3 phase 208 wye source, The welder itself is single phase 208 on 1 &3, and there is some kind of axulliry equipment like a big wire feed or a fume extractor connected to 2 & N????

Am I reading the original post right?
 
It is basically a multiwire feeder to the disconnect and two 120 volt branch circuits after that. Sounds like one could add a third 120 volt branch circuit if they wanted to
 
It is basically a multiwire feeder to the disconnect and two 120 volt branch circuits after that. Sounds like one could add a third 120 volt branch circuit if they wanted to.
No, it's not two 120V branch circuits. It's one 208V branch circuit and one 120V branch circuit. Read it again.
 