We use 3Ø to 1Ø feeder meter banks.
What am I looking at? Where did the blue phase go? What is that microchip thing?
We use 3Ø to 1Ø feeder meter banks.
What am I looking at? Where did the blue phase go? What is that microchip thing?
That is a meter bank.
The little round black things are CT's which digitally read the load for each apartment. The blue phase is present on the meter bank feeder but since the loads are all 1Ø only black and red are used for each apartment feeder. As Bob stated earlier the 1Ø loads are distributed evenly by being connected A-B, C-A, and B-C.
That has to be about the neatest panel I have ever seen.
Most of the ones I get to work in look like a wire shredder vomited 10lbs of cable in a 5lb cabinet.
Since all or most of the loads will be single phase to neutral, it won't ever be balanced except by coincidence.Can yall help clarify this for me? We have never installed single phase on a 3 phase and we dont' understand how it will work. How do you attach the single phase meter stacks to the main so that its all balanced?
There was a newly constructed apt building here in Austin a few years ago that was wired that way, but unfortunately there was a mixup in communication with the POCO and they installed a 240V high leg transformer instead of a 208/120V tranny. Oops.That is a meter bank. The little round black things are CT's which digitally read the load for each apartment. The blue phase is present on the meter bank feeder but since the loads are all 1Ø only black and red are used for each apartment feeder. As Bob stated earlier the 1Ø loads are distributed evenly by being connected A-B, C-A, and B-C.
That is a meter bank. The little round black things are CT's which digitally read the load for each apartment. The blue phase is present on the meter bank feeder but since the loads are all 1Ø only black and red are used for each apartment feeder. As Bob stated earlier the 1Ø loads are distributed evenly by being connected A-B, C-A, and B-C.
Why wouldn't it be? I have seen 1P3W panels on A and C on a high leg service; what's the diff?Ok, I will bite. Is that even legal? :blink:
Why wouldn't it be? I have seen 1P3W panels on A and C on a high leg service; what's the diff?
Since all or most of the loads will be single phase to neutral, it won't ever be balanced except by coincidence.
Wow, that looks very clean, Rob!
Still a panelboard to the NEC
Never seen that set up.
Is it utility metering or is it landlord metering?
I posted the photo to depict what is common in apartment buildings, 3Ø risers and panelboards with 2 pole CB's feeding all 1Ø apartment loads.
Not common here, sub metering of new dwelling units not allowed.
We would have something like this in the basement or on each floor with three phase in and single phase out.
That is a meter bank. ....
Sub metering for the purpose of selling power is likely what is not allowed. If there still is a utility company meter ahead of the submetering, then the owner (where applicable) can't sell power to each tenant but can still monitor what they use for his own purposes. If utilities are included in the rent/lease and utilities increase over time then one can adjust the rent/lease fees.Not common here, sub metering of new dwelling units not allowed.
We would have something like this in the basement or on each floor with three phase in and single phase out.