That makes the alum wire bad?The customer replaced the house panel with a larger panel with 125A bus 3 years ago during a remodel, re-using the existing #4AL feeder.
That makes the alum wire bad?The customer replaced the house panel with a larger panel with 125A bus 3 years ago during a remodel, re-using the existing #4AL feeder.
Sounds like SEU cable. If that is the case your feeder is only 3 wires (2-insulated and 1- bare) The cable needs to be replaced with a 4 wire cable.And yes, this is a feeder. And it appears now that it is definitely safe to put #4AL on a 60A CB.
I remember the spiral wrapped stranded neutral and assume that that ID's it as SE cable. Am I wrong to assume this? The wire is from 1974.
Has AL SE cable always been rated at 75* C?
Yes it is 3-wire, which never should've been used in this application. (Residential electricians in 1974). I told the homeowner that It needs to be 4 wire when the main panel was replaced last fall, and that it needs to have the neutrals isolated from the grounds on a separate ground bar at the sub-panel.Sounds like SEU cable. If that is the case your feeder is only 3 wires (2-insulated and 1- bare) The cable needs to be replaced with a 4 wire cable.
Did you mean 65 amps?Addressing your direct question. Assuming the #4 AL SE has 75° conductors and the terminations are rated 75° (both highly likely siktuationsP), the cable can be used at it's 75° ampacity of 65 amps and, if the actual load does not exceed 75 amps, it can be protected by a 70 amp breaker (assuming the panel buss in rated that high)
When the terminations are not written down you need to assume 60° till 100 amps. Is this what you're thinking about? If so almost all breakers and modern panels have 75° rated and identified lugs.The 70A question came up when it came to feeders smaller than 100A in residential applications, and the old rule about treating them as if they are only rated to 60* C regardless of the actual insulation rating on the wire type used. SE cable is rated for 75*C applications, but if I understand what I've read, NEC doesn't allow it to be on a 70A breaker... that's what I'm seeking clarification on.
Sometimes the deeper you dive into the NEC, the more confusing it becomes.
yes//typoDid you mean 65 amps?
No, I know about the terminations and these all are 75*C... SE cable ampacity rating as a residential sub-panel feeder is the question: is it limited to 60* ampacity in this case even though the SE cable insulation is rated higher? Much of the posts I have read here indicate SE is treated thr same as NM-B at 60* C rating onlyWhen the terminations are not written down you need to assume 60° till 100 amps. Is this what you're thinking about? If so almost all breakers and modern panels have 75° rated and identified lugs.
2017 2020 and 2023 say if it's bigger than 10awg you're good with 75° so long as the conditions allowing it are followedNo, I know about the terminations and these all are 75*C... SE cable ampacity rating as a residential sub-panel feeder is the question: is it limited to 60* ampacity in this case even though the SE cable insulation is rated higher? Much of the posts I have read here indicate SE is treated thr same as NM-B at 60* C rating only
The run in this case is through the garage attic, breezeway, house attic, and down into an interior wall in the laundry room. Apparently the code has been modified beginning in 2008, going back & forth several times on this. Trying to sort through all the nuances and contradictions in the Code has given me headaches and doubts as to whether or not the 75* ampacity column applies to SE in this case.
Thanks! That makes sense.2017 2020 and 2023 say if it's bigger than 10awg you're good with 75° so long as the conditions allowing it are followed
Nmb is always 60 for ampacity but 90 for derating purposes. This is no matter the size or conditions.Thanks! That makes sense.
Now- does that apply to NM-B larger than 10awg?
What about original NM? I was taught that it was only rated to 60* regardless of awg size.
Thanks for the confirmation.2017 2020 and 2023 say if it's bigger than 10awg you're good with 75° so long as the conditions allowing it are followed
That explains why SE is often seen on residential HVAC & large appliances. It allows smaller wire than NM provided the lugs and eqpt are rated at 75*C and ambient temp derating is in line.Nmb is always 60 for ampacity but 90 for derating purposes. This is no matter the size or conditions.