#2 aluminum SER? Might be a bit small. We've been in a heat wave, hitting 100* plus here for 2 weeks, and the attic has to be a lot hotter.
Normally it is low-to mid 90's this time of year, not hitting 100* until late July or August. Last summer was brutal as well. The wire will be through the unfinished garage rafters then in the attic so I'm not sure where to draw the line on ambient temp under these circumstances.
#2 aluminum SER derates to 91A at 40*C/104*F ambient, dropping to 82A at 50*C/122*F ambient.
#1 aluminum SER derates to 100A at 45*C/113*F ambient or 94.3A at 50*C/122*F ambient.
1awg AL may be reasonably priced due to popularity/availability. I'll have to price it out when the supply houses open Monday.
I know what you mean about a "not great job", but in this case he isn't trying to tell me what's right... he's just dealing with accepting the cost. Wife Acceptance Factor comes into play here too
.
A 90A would be a big improvement and could very well be the ticket. 80A might even do him justice, but at this point I'd rather see him spend the money on bigger wire than to wade through all the load calculation and guessing what he might add on to his house next. One and done is my M.O.