If a single set of 3-wire, single-phase, service-entrance conductors in raceway or cable supplies a one-family, two-family, or multifamily dwelling, the reduced conductor size permitted by 310.15(B)(6) is applicable to the service-entrance conductors, service-lateral conductors, or any feeder conductors that supply the main power feeder to a dwelling unit.
This section permits the main feeder to a dwelling unit to be sized according to the conductor sizes in Table 310.15(B)(6) even if other loads, such as ac units and pool loads, are fed from the same service. The feeder conductors to a dwelling unit are not required to be larger than its service-entrance conductors.
Exhibits 310.7 and 310.8 illustrate the application of 310.15(B)(6).
In Exhibit 310.7, the reduced conductor size permitted is applicable to the service-entrance conductors run to each apartment from the meters.
In Exhibit 310.8, the reduced conductor size permitted is also applicable to the feeder conductors run to each apartment from the service disconnecting means, because these feeders carry the entire load to each apartment.
I have flipped on this one a few times. I think that the section needs revision. Using the term "main power feeder" and then defining that term in a way that does not say anything about being the "main" supply to the dwelling unit is the cause of the confusion. I believe that the panel's intent is that the reduced sizes cannot be used for "subpanels", but the code wording does not support the panel's intent. I believe that the wording in the code book, permits the reduced sizes for all dwelling unit lighting and appliance branch circuit panel feeders.Don, this is another occasion where we will have to disagree, but I must ask, when did you change your opinion, this was not your stance in November on another forum.