Dennis Alwon said:Here is an interesting scenario for those who use aluminum for se conductors and feeders.
400 amp meter base with 2- 200 amp panels. In the past we could run 4/0 aluminum to each panel and everyone would be happy. Then the CMP changed art. 310.15(B)(6) to clarify that in order to use T310.15(B)(6) the conductors must carry the full load of the service. So for a 200 amp service 4/0 SE cable is still good if it carries the full load of the service. Why? Because T310.15(B)(6) allows 4/0 aluminum for 200 amps and se cable is an acceptable wiring method.
Okay now back to the 400 amp service stated above. Se cable cannot even be used. Why because 4/0 seu to each panel will not satisfy Art. 310.15(B)(6).
Now we must use Table 310.16 which states we must use 300 KCM aluminum for 200 amps. 250 KCM is only good for 170 and 175 is next higher size breaker so you cannot use that conductor. 300 KCM is what must be used.
Let's install the seu cable from the 200 amp and use firecaulk around it into the building and that does not change a thing even though that is the main reason - as Bob pointed out- that SE cable has been derated to 60C.
So 200 amp service 4/0 se cable is fine for a SFD however 350 KCM must be used for a 400 amp service that utilizes 2-200 amp panels.
This is what I was getting at in my first post (#8).:smile:
steve