shortcircuit2
- South of Bawstin
Is two 200A panels at other end a possibility?
Violation of 225.30
Outright, yes. However, 225.30(B)(2) opens up a possibility, however thin that may be. The only thing in question is probability. Just need AHJ blessing. Granted, it may not be an intended possibility for this size building... but it is not written that way. It goes without saying, but you'll never know unless you ask.Violation of 225.30
Which Utility?
And given the meter main named is 2/200 only, what other option is there? Does Milbank offer a 400A 4-pole breaker?
So they are listed as a single unit?They do not. I called Milbank today and asked if the two 200 amp breakers were parallel per 240.8 and they said yes.
Disconnect at meter is a utility requirement for remote mounted meters
Here is what the 2010 National Grid spec book says...
5.1.7.2 Meter pedestals are free-standing units intended to be mounted outdoors on a concrete pad in
conjunction with underground wiring. If a free-standing meter pedestal is used, it shall extend a minimum
below the finished grade or ground line with stabilizing means extending below the frost line to ensure
that the meter mounting stays in a plumb position. See Section 7 for further details. Meter pedestals for
self-contained metering must be listed devices and shall also incorporate circuit breakers, but these are
not intended to replace the service disconnecting means required at the building.
Here is a link to National Grids requirements...
https://www.nationalgridus.com/niagaramohawk/non_html/constr_esb750.pdf
A couple factors are in play. Just as typical disconnects are not rated for disconnect under load, meters are no different. It's also an extra layer of assurance that nothing on the load side will backfeed the socket while the meter is removed. For example, it's not unheard of for a home owner to backfeed the system with a generator and not have the required interlock.I have talked with the engineers from national grid that look at the install before they send the line crew. They want the disconnect. They say its for the safety of the meter people in case they need to remove the meter. I question that because they don't require the disconnect if the meter is on the house. Whats the difference to the meter person? If they can pull the meter without the disco at the house why is a remote meter different?
That could be an option, if acceptable to the POCO.I would think a meter socket with a bypass would be sufficient to allow them to service/check/replace an in use meter socket
My guess, is if the meter is away from the house they want customer to be able to disconnect the feed from meter to the house without having to call POCO, this makes their maintenance responsibilities end at the metering equipment.I have talked with the engineers from national grid that look at the install before they send the line crew. They want the disconnect. They say its for the safety of the meter people in case they need to remove the meter. I question that because they don't require the disconnect if the meter is on the house. Whats the difference to the meter person? If they can pull the meter without the disco at the house why is a remote meter different?
Anyways If I want it hooked up I have to have the disconnect. They require it for any remote meter of any amperage.![]()
Sounds to me like they couldn't think of a better answer. If they want no load when installing/removing a meter they will require disconnecting means for all meters.Talked to a National grid engineer to find out why the disconnect. He said it protects the meter person if they install a meter and the load side of the underground has a fault, they wont end up creating a dead short. The person can install the meter and turn on the breaker. If the customers underground has a fault the breaker will trip, saving the meter person from an arc. I guess if the meter is at the house they figure its less likely to have a fault.