Not sure about that, a 400A panel should be rated at 400A continuous for a SUSE rating IMO.
No, they are not unless you order a panel overcurrent devices with a 100% rating.
Not sure about that, a 400A panel should be rated at 400A continuous for a SUSE rating IMO.
No, they are not unless you order a panel overcurrent devices with a 100% rating.
I just find the use of the term 400(320) to be confusing and I'm wondering why it's even noted that way. A 400 amp load calculation means a 400 amp meter enclosure.
Read the info inside the 400 amp meter base. If you go to the supply house around here and ask for a 400 amp meter base they hand you one that states 320 amps. Now why they sell the 400 amp base at the 320 rating and the 200 at the 200 amp rating instead of 160 amps rating- I don't know.
Not sure how the 3 phase meters are rated. Certainly in a home you would rarely be close to 160 amps continuous on a 200 amp service.
When I install a 200 amp meter base I understand that is only rated 160 continuous. It is still, IMO a 200 amp service. If someone has need of 200 amp continuous then I would go up to 400 amps or possible 300 ampsI have to ask if the 400 amp service is truly a 400 amp service, or a 320 when it is installed. A true 400 amp service will take a K base or some transformer rated metering. an S Base is only rated for 320 continuous.
When I install a 200 amp meter base I understand that is only rated 160 continuous.
I have to ask if the 400 amp service is truly a 400 amp service, or a 320 when it is installed. A true 400 amp service will take a K base or some transformer rated metering. an S Base is only rated for 320 continuous.
Not really. It is relevant if you have over 160 amps of continuous load in the building. Basically the meter is not rated to carry a continuous load over 160 amps.I agree it's a 200 amp service, unless I'm missing something the use of the wording 160 amps continuous is irrelevant.
Not really. It is relevant if you have over 160 amps of continuous load in the building. Basically the meter is not rated to carry a continuous load over 160 amps.
Not really. It is relevant if you have over 160 amps of continuous load in the building. Basically the meter is not rated to carry a continuous load over 160 amps.
It may be unlikely scenario but that would be when it comes into play--
Not really. It is relevant if you have over 160 amps of continuous load in the building. Basically the meter is not rated to carry a continuous load over 160 amps.
It may be unlikely scenario but that would be when it comes into play--
sorry about the confusion... it is feeding (2) 200 amp panels
Yes that's my point. The 200 amp meter would not be good in that case even though the load is under 200 ampsIn that case the NEC load calculations would have required more than a 200 amp service.
Yes that's my point. The 200 amp meter would not be good in that case even though the load is under 200 amps
I am saying if the load is continuous at 170 amps and you had a 200 amp breaker that is rated 100% then you could not use the 200 amp base. Highly unlikely I knowI am very confused,:? the load would not be under 200 amps it would be over 200 amps.
We do have a member saying that the 200 amp base is rated 200 amps continuous. I will have to check as it was not always that way.