Was it this one?
georgestolz said:Now, here is the thing I am going to offer about this; every time this discussion comes up, it invariably leads to "What if someone installs a 7th breaker?"
Is a 7 handle service unsafe? We're allowed more than six for some purposes, mentioned in 230.71. It just tickles me to hear the "horrors! horrors!" hand-wringing because a code rule could be violated at some point in time.
augie47 said:I have been in this game a LONGGGGGGG time and have always thought MLO service panels were "weak links" and a major oversight by CMPs, however, I must admot I have not actually witnesses a "meltdown" in thes e many yeasrs of inspecting. Some fellows from areas with heaver loads might.
Has anyone actually experienced a problem with this ?
iwire said:David, Larry. I would say that 18 is not the limit.
Some shunt trip breakers use 4 spaces, that brings us to 24 spaces needed to reach six disconnects.
Dennis Alwon said:georgestolz said:Now, here is the thing I am going to offer about this; every time this discussion comes up, it invariably leads to "What if someone installs a 7th breaker?"
My response, setting the six-handle rule aside for a moment (which I have always faithfully respected): So what?
Is a 7 handle service unsafe? We're allowed more than six for some purposes, mentioned in 230.71. It just tickles me to hear the "horrors! horrors!" hand-wringing because a code rule could be violated at some point in time.
Interesting that you say this because I was just downstairs telling my wife how absurd it is to think that a fireman or anyone else couldn't turn off an entire 42 circuit panel in 5 seconds. Many of them just pull the meter anyway, of course if there are CT's that won't work....
I am not advocating breaking the rules nor do I ever break this one but as George says "Big Deal". There are a lot more issues to be concerned about than this--- like the lack of EGC on those outdoor post lights in a recent thread.
jim dungar post #36 said:First, the NEC does not apply to the manufacturing of a panelboard.
Second, how do you know that the manufacturer did not submit "some" combination of breakers and handle ties that provides for only 6 operations of the hand?
While I don't think it is a good design to for this 40 circuit MLO panel application, I cannot call it a 110.3(B) code violation if I see the UL listing allows it.
dnem said:As of right now, I don?t believe UL listing allows it.
jim dungar said:So you are still working on your own personal beliefs.
jim dungar said:Have you gone to any local electrical supply house and looked at the MLO panels they have in inventory? I have seen many brands (SQD, C-H, and Siemens included) that all have UL labels on panels similar to the one under discussion. It is unlikely that most manufacturers have been mis-applying UL labels for so many years.
jim dungar said:Have you notified UL about this supposedly mis-applied label?
dnem said:It's not working on personal beliefs. . It's working with the information that you have. . The best information that I have says that the panel discribed by the original poster has been installed in violation of its UL listing.
There are certainly many MLOs that are listed as suitable for service equipment. . Are you specifically asking me about 40 and 42 slot MLO panels ?
I have discussed this with UL representatives and come away very unhappy with their replies.
romeo said:Thank you for your response. That is what I am doing now, I expect to hear from the power company Eng. tomorrow.The breakers have 10,000 AIC rating,if the available fault current does not exceed 10,000 the service will pass.
Just to let everyone know, I am not a this is my town kind of inspector, if I am not able to provide a code section that has been violated I will pass the job.
jim dungar said:What was Ul's reponse when you told them a manufacturer had mis-applied a label?
jim dungar said:Yes, have you looked at UL labels on any new MLO panels with 30-40 circuits?
jim dungar said:That thread seems only to address the NEC definitions of panelboards and the "recent" NEC prohibition of not more than 2 disconnects for a residence.
dnem said:There is no 2 disconnect limit for a residence.
dnem said:The limit for all buildings is 6.
David
iwire said:Now David I know that you know we can have more than 6 disconnects in one location and we can certainly have more than 6 service disconnects on the same building in different locations.![]()
j_erickson said:Let me start by saying I know Romeo personally, and I like and respect him very much. And he is a good and thorough inspector.
But I have to ask: Are you checking the AIC rating for every installation? Or are you doing so for a hidden agenda? If he had agreed to change the original installation to one with a main, would you have checked the AIC rating? With all due respect, it seems like you are doing this because you "don't like" the install. (I don't blame you for not liking it, BTW)
And please don't take this out on me next time I'm in town.![]()