mdshunk said:
Yeah, I doubt that very much. 25 RV's is closer to 825 amps.
How in the world did you arrive at that figure?
My calculations using 551.71 and 551.73 came out to 490 Amps:
25 sites total
20% (5) required to be 50 Amp using 9600 VA = 48000 VA
50% (17.5 or 18) required to have 30 Amp using 3600 VA = 64800 VA
remaining sites (2) using 2400 VA per site = 4800 VA
Total: 117600 VA
@ 240 Volts = 490 Amps.
Using the demand factors allowable from table 551.73 (42%) I show a minimum required service of 206 Amps.
While I am not advocating installing the =minimum= allowable service (which should not be used in this case), specifying a 320/400 Amp service is well within the
Code requirements.
Now, if the actual number of sites are using larger outlets (such as all of them with the 50 Amp receptacles) the totals will be different. This is the job of the electrician on site to determine when performing his load calculations, which I asked for in an earlier post in this thread.