Iam installing a 400 amp service at a RV park using a 320 continous service meter socket. (2) #500mcm copper and (1) 350 neutral with a 1/0 ground wire to meter socket using a 2 1/2" rigid conduct. From meter socket to a 8"x8"x48" raceway where we will make taps for (2) 200 amp disconnects fuseible. Also a 100 breaker panel on raceway. The 200 amp disconnects feed existing panel in the park does this look right thank you .