hardworker
A 400 amp single phase subpanel is being installed 70 ft. from the main panel. What awg size of wire and what size of conduit is correct?
Its this a test question? Pretty basic question for most electricians.A 400 amp single phase subpanel is being installed 70 ft. from the main panel. What awg size of wire and what size of conduit is correct?
Just trying to see if there is more than one way to go about it.
At 70' voltage drop shouldn't be too much of an issue. There are a few options, as mentioned 500 kcmil gets you 380 amps so if your load isn't greater than 380 you're OK with 500's. If you want the full 400 amps then you can opt for 600 kcmil @ 420 amps. Or you could use two sets of #3/0 in separate raceways which gives you 400 amps or you could use parallel sets of #3/0 in one raceway and end up with 360 amps. If you like smaller conductors you could use 3 sets of #1/0. in 3 raceways @ 450 amps or one raceway @ 357 amps. The ampacities that are less than 400 amps would need to comply with the next standard size up rule.
As you can see there are many variables depending on the parameters of you installation.
If it is my choice, and copper is required, I would run 2 parallel sets of #4/0 Cu with a #3 Cu ground, all THWN-2, in a common 3" conduit, to get use of the full 400A.
Under the above scenario what is the exact amount of amps that would be achieved?
There are many ways to go about it.Just trying to see if there is more than one way to go about it.
It would depend on how many CCC there are which we do no have enough information to say for sure. Assuming three phase with the neutral not a CCC we have 6 CCC which is a .8 derating from the 90 degree value or 416 amps. If the panelboard is truly a 400 amp, 408.36 would not allow you to exceed a 400 amp OCPD to supply it.
This is single phase.