400 amps underground service 280' from transformer to meter

Merry Christmas

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The load calculation has nothing to do with the length of the conductors. Are you trying to do a voltage drop calculation?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
It's odd to hear the customer has to provide & install the conductors for UG. I deal with 5 or 6 different POCOs and all of them install the conductors. Some require us to provide the conduit but none require us to install the conductors. We pull a string and leave it in the conduit, POCO takes it from there.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It's odd to hear the customer has to provide & install the conductors for UG. I deal with 5 or 6 different POCOs and all of them install the conductors. Some require us to provide the conduit but none require us to install the conductors. We pull a string and leave it in the conduit, POCO takes it from there.
We have had to provide and install the underground from a pad mount to the service equipment for commercial services for a long time. The only think the utility does is terminate at the transformer. Recently they have stated to require that for dwellings too.
 
It's odd to hear the customer has to provide & install the conductors for UG. I deal with 5 or 6 different POCOs and all of them install the conductors. Some require us to provide the conduit but none require us to install the conductors. We pull a string and leave it in the conduit, POCO takes it from there.
the other way around for me. The idea of the Poco pulling conductors to the meter socket baffles me, I think I've seen it once in
25 years!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IF your calculated load is actually 350 amps (rare on residential), to maintain a 3% voltage drop you would need parallel 300 kcmil AL and, if you don't reduce the neutral, it would take a 3" PVCconduit (assuming there is some Sch 80)
 