I agree it is intended to... but Exception No. 3 is not worded explicit enough to say absolutely. After all it is an exception. If you look at service entrance conductor requirements for ampacity, it is based solely on calculated load, with no consideration for OCPD rating.
SE conductor sizing based on calculated load is good practice, one used for most conductor sizing. Then 230.90(A) provides sufficient guidance for OCPD rating.
I understand your angle with the proposal. But I don't think its necessary. I see the wording in 230.90(A) as descriptive enough to disallow a single overcurrent device in a multiple switch service from being larger than the SE conductors feeding the assembly.