kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Do whatever you wish. If you don't want to get POCO or inspector involved down the road, then installing the second 200 amp now gets you past that part if you need it later down the road. Otherwise you essentially only have a 200 amp service if you do what you say you wish to do. How POCO and/or AHJ determines the size for rate purposes, inspection fee purposes, etc. may still vary some from location to location, but if you install a single 200 amp main breaker to supply all loads - you can not use more then 200 amps for very long without it tripping - so you have limited yourself to making 200 amps all that is available. If POCO wants to charge you a higher rate for a higher capacity service - if saving $$$ is the main goal here you may want to change other equipment as well to get on a lower rate - of course you still need to look at return on investment before making this decision. Most residential services usually are at same rates whether 100 amp or 600 amps, but throw in something larger then that or a three phase supply and they may put you in a different rate classification.