I have a 400A I-line molded case main breaker that is sporadically tripping, it has tripped twice in the last two weeks with anywhere from 2 days to a week between trips. The main feeds 4-30A feeder breakers and 1-40A feeder breakers. These feeders in turn feed a couple exhaust fans and some heater strips. The panel was installed prior to 1990 and the main has likely only been operated a few times, the issue supposedly started after the main was locked out. The interior of the panel appears to be free of any discoloration or obvious issues, the equipment downstream continues to run when the breaker holds and the trip indicator on the breaker itself doesn't register any fault conditions. I have tested the breaker by starting all the fans and heater strips at the same time and the breaker still holds. I am thinking it is an internal issue to the breaker that requires replacement but I wanted to see if anyone else had a suggestion before I recommend spending $20k on a new breaker(or $10k to downgrade to a 200A main). Please let me know if anyone has any suggestions, thank you.