Along with what COW said, have your supplier price a whole new unit as if it were a new project complete with all new breakers. The prices come down considerably when they know they are bidding.
the replacement that squareD quoted came in at $19k.
I try not to purchase large framed breakers directly from the manufacturer unless someone is holding a gun to my head. Their markups are insane once they know you have their gear installed and you need parts for it. I don't like those games.
I try 3rd party resellers/testing firms, whether it's new or used/tested surplus first. If that doesn't pan out, then I head over to the manufacturer knowing what comes next, is going to be sticker shock.
20k for a 400 amp breaker is nowhere near reasonable.
Thank you for the responses everyone. We have a breaker testing and rebuild shop on site so I'm gonna look at getting the panel on a temporary generator while we pull the breaker and test it. If the breaker ends up being faulty I will definitely be looking into replacing it with a set of fuses, another panel, or seeing if i can find an adapter kit to make a different breaker fit since the replacement that squareD quoted came in at $19k. Zog I appreciate your offer on the repair but unfortunately my employer will not let us repair(or have anyone else repair) molded case breakers.
It's not a breaker repair , it's a trip unit repair, or you can replace the trip unit with a new one. A new replacement for that breaker (PJA) should be around $5k (19k is insane)