And so in their opinions the other conductors aren't a concern.Mine is clueless, but the localities agree, because the tag makes it inaccessible.
And so in their opinions the other conductors aren't a concern.Mine is clueless, but the localities agree, because the tag makes it inaccessible.
Mayhaps they think only GEC terminations need inspection.And so in their opinions the other conductors aren't a concern.
Yep, that's the one that will cause mayhem for sureMayhaps they think only GEC terminations need inspection.
Then the unbroken/unspliced rule applies only to the conductor from the bar to the main electrode.At this point I just want to install a grounding busbar in the garage and take all of the GECs to it.
True. I just feel like there isn’t really a fully safe and compliant install with a 400a meter and 2 service panels. I wish my company would just let us install a 400a service panel….Then the unbroken/unspliced rule applies only to the conductor from the bar to the main electrode.
Why?I just feel like there isn’t really a fully safe and compliant install with a 400a meter and 2 service panels.
I don’t know. Feels like it’s hard to tell who to trust. I could blindly follow my boss who has been wrong about code many times but I want to do things right. I come here looking for answers and I’m more confused than ever. Maybe you guys are giving me the answer and I’m missing it.Why?
I meant which part of an installation do you feel is difficult to comply with code about?I don’t know. Feels like it’s hard to tell who to trust.
I think grounding/bonding two panels using the same GES. I’m also reading elsewhere online about the parallel neutral path and it almost seems unavoidable with this configuration.I meant which part of an installation do you feel is difficult to comply with code about?
You need a single GES anyway- all the qualifying grounding electrodes* need to be bonded together, so in essence those make a single GES for everything. Not quite on-point, but also imagine where a structure has a 408Y service, a 208Y service and a 240D service; they're all going to use the same GES.I think grounding/bonding two panels using the same GES. I’m also reading elsewhere online about the parallel neutral path and it almost seems unavoidable with this configuration.
Many people struggle with grounding and bonding multiple service disconnect enclosures. I am not sure why, it says right in the code 250.64(D) "Building or Structure with Multiple Disconnecting Means in Separate Enclosures"......I don’t know. Feels like it’s hard to tell who to trust. I could blindly follow my boss who has been wrong about code many times but I want to do things right. I come here looking for answers and I’m more confused than ever. Maybe you guys are giving me the answer and I’m missing it.
Keep in mind that many jurisdictions, such as VA, don't allow landing GECs in the meter base.Along with the illustrations DSG posted here is another option , just imagine another panel on the left side of the meter.
View attachment 2571493
I’ve only seen one area where I live require it. Otherwise I’ve always been told to avoid it.Keep in mind that many jurisdictions, such as VA, don't allow landing GECs in the meter base.