I have an HVAC condensing unit with a bad 480VAC 3PH 60 HZ motor and the only suitable replacement I can find quickly (less than a 52 week lead time) is a 400VAC 3PH 50 HZ motor. My understanding is that it will work but isn't recommended. Any thoughts or opinions or examples ?
Are you replacing the entire condensing unit, or just one motor?
Turning a fan at 120% of its design speed will consume between 144% and 172.8% as much power. At best, it will be noisy and waste energy. At worst, something will break and/or the motor will fail prematurely.
Turning a compressor at 120% of its design speed will pump ~120% more refrigerant. The condenser and fan will then be undersized, throwing the system out of balance, resulting in higher temperatures and pressures that probably will result in premature compressor failure.
If the entire unit will be replaced, the relays and transformers inside will be operating at 120% of their design voltage, resulting in higher currents and temperatures.
But the cost of premature equipment replacement will pale in comparison to the cost of wasted energy. HVAC consumes a LOT of energy; any sort of Appalachian Engineerin' that reduces efficiency will be very expensive in the long run.
Bring in a mechanical engineer for a consultation. HVAC equipment is almost always oversized and a smaller unit may very well provide adequate performance. (and also energy savings)
Note that when speed is raised above the base speed of 50Hz motor, a vfd operates the motor in constant hp mode ie torque is reduced. ...
This is not possible with a fan motor. If you turn a fan at a higher speed, it will consume more torque and power. Either the motor will supply the additional torque & power, or it won't turn at the selected speed.