can someone explain this to me?
408.36(A) Snap Switches Rated at 30 Amperes or Less. Panelboards equipped with snap switches rated at 30 amperes or less shall have overcurrent protection of 200 amperes or less.
NolaTigaBait said:oh, ive never seen one of those panels before....thats where my confusion came from....so on a main lug panel(used as service equipment) i can have any size breakers that i want with no main protection?
walkerj said:Yes, as long as they don't exceed the rating of the panel
iwire said:Do you have a code section in mind?