Gogreen100
Member
In an existing house with 1 200A service, is going to have a new dual fuel heating system put in. 1 gas forced air furnace as back-up. 1 20KW plenum heater and 1 20KW boiler (floor heat) as primary.
The job has been put together by a local firm and electrical specs sent out for contractors to bid on.
1-Install 2nd 200A electrical service. 230.2(D)
2-Wire 40KW of new electric heat to new service.
3-Etc.
Question:
Is 40KW to much for a 200A 120/240 1ph service?
Can you derate any of the heat?
Do you have to add 125% on to the calcutated load?
220.51 states it shall be calculated at 100%.
I live in border city and have asked both local inspectors and have got 2 different answers.
The job has been put together by a local firm and electrical specs sent out for contractors to bid on.
1-Install 2nd 200A electrical service. 230.2(D)
2-Wire 40KW of new electric heat to new service.
3-Etc.
Question:
Is 40KW to much for a 200A 120/240 1ph service?
Can you derate any of the heat?
Do you have to add 125% on to the calcutated load?
220.51 states it shall be calculated at 100%.
I live in border city and have asked both local inspectors and have got 2 different answers.