Pick the one that applies to your installation.
The installation in question uses a mogul base lampholder and a cord and plug remote ballast mounted on a wall, it is not above the fixture as would be required in 1.
The mogul base bumps it into 2, however since it is cord connected I am thinking both 1 and 2 apply.
I am concerned about the use of 6-15 receptacles on a 30A or 50A branch circuit for HID lighting. There is supplementary protection built into the ballast which is what the reference to 240.5(A) is as well as UL listing requires ballast cores to have thermal protection.
This paragraph 1 I think wants the receptacles above the light. If the receptacle can be down on a wall what is to prevent another type of equipment from being plugged in later on?
The UL information is here:
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html
The Ballasts are here:
http://www.lumatek.co.uk/index.php/products/electronic-ballasts.html
(this is for use in a class I am putting together)