Member
I apologize for the length of this post, but I've come across an issue the nobody seems to be able to definitively answer. I'll admit that it's a bit self-serving, in that my company manufactures light CFL fixtures (inlcuding recessed downlights) that appear to meet the code in a unique way, along with other safety features.
As far as I can read, there are two classes of covered fixtures (retyped from
the code, only adding carriage returns):
====================
fluorescent luminares (fixtures) that utilize double-ended lamps and contain ballast(s) that can be serviced in place
or
ballasted luminares that are supplied from multiwire branch circuits and contain ballast(s) than can be serviced in place
=====================
Please let me know what you think. the only response I have received from the industry "experts" is that it only covers double-ended lamped ballasts; they seem to ignore the second group outlined above.
Someone I know asked Howard Wolfman of OSI and Chair of the NEMA Lighting System Division. Here was his response:
"It is my understanding that the US NEC Code Panel has concluded that the luminaire disconnect applies only to double ended fluorescents, for all covered luminaires installed after January 1, 2008. Canada, on the other hand, requires disconnects for all luminaires manufactured after June 1, 2007, and effective 1/1/2010, is also adding CFLs, but it is possible that this requirement may be removed from the Canadian Electrical Code."
If this is true, and it only applies to double-ended fluorescents, then I have a few questions:
1- What is the purpose of the second group listed above (after the -OR-)? The presence of a common descriptor ("Contain ballasts that can be serviced in place") would indicate a separate second group, and the absence of the descriptor "utilize double-ended lamps" would indicate it is NOT applicable to that second group.
2- If the purpose of the code is to provide a means for safer fixture maintenance, why does it not apply to CFL's? Maintenance on those fixtures is as dangerous as double-ended fluorescents, aren't they? So I guess it's not OK for people to get hurt while working on double-ended lamps, but fine if they're hurt working on CFLs?
3- All the responses I've seen include qualifiers like "it is my understanding" leading to clouded facts. If it's in the code, then it's there... If it shouldn't be in the code, then it should have been taken out by now, especially since it goes into effect in less than six months.
4- If a building is erected after 1/1/08 that has CFL fixtures that do NOT have the disconnect, and a worker gets electrocuted while working on one of the fixtures, would YOU want to have to explain to a jury why the fixture didn't have the disconnect, given the code as it is written? What would YOU say?
I appreciate everyone's responses.
As far as I can read, there are two classes of covered fixtures (retyped from
the code, only adding carriage returns):
====================
fluorescent luminares (fixtures) that utilize double-ended lamps and contain ballast(s) that can be serviced in place
or
ballasted luminares that are supplied from multiwire branch circuits and contain ballast(s) than can be serviced in place
=====================
Please let me know what you think. the only response I have received from the industry "experts" is that it only covers double-ended lamped ballasts; they seem to ignore the second group outlined above.
Someone I know asked Howard Wolfman of OSI and Chair of the NEMA Lighting System Division. Here was his response:
"It is my understanding that the US NEC Code Panel has concluded that the luminaire disconnect applies only to double ended fluorescents, for all covered luminaires installed after January 1, 2008. Canada, on the other hand, requires disconnects for all luminaires manufactured after June 1, 2007, and effective 1/1/2010, is also adding CFLs, but it is possible that this requirement may be removed from the Canadian Electrical Code."
If this is true, and it only applies to double-ended fluorescents, then I have a few questions:
1- What is the purpose of the second group listed above (after the -OR-)? The presence of a common descriptor ("Contain ballasts that can be serviced in place") would indicate a separate second group, and the absence of the descriptor "utilize double-ended lamps" would indicate it is NOT applicable to that second group.
2- If the purpose of the code is to provide a means for safer fixture maintenance, why does it not apply to CFL's? Maintenance on those fixtures is as dangerous as double-ended fluorescents, aren't they? So I guess it's not OK for people to get hurt while working on double-ended lamps, but fine if they're hurt working on CFLs?
3- All the responses I've seen include qualifiers like "it is my understanding" leading to clouded facts. If it's in the code, then it's there... If it shouldn't be in the code, then it should have been taken out by now, especially since it goes into effect in less than six months.
4- If a building is erected after 1/1/08 that has CFL fixtures that do NOT have the disconnect, and a worker gets electrocuted while working on one of the fixtures, would YOU want to have to explain to a jury why the fixture didn't have the disconnect, given the code as it is written? What would YOU say?
I appreciate everyone's responses.