I am trying to come up with language to create an exception to 430.102(A) for the 2011.
The problem is that every controller needs a disconnect, unless over 600V or unless there is a group of controllers.
Scenario: Cord and plug connected disposal. The cord and plug is the disconnect for the disposal, and the switch above the countertop is the controller (see controller] definition). The controller (switch) requires a disconnect within sight of the controller. In other words, you need a switch in front of the switch, to act as a disconnect for the switch!!!
What should the exception be?
Dwelling units?
Controllers with a marked "off" postition that switches all ungrounded conductors?
Controllers that meet the requirements to be used as a disconnect (430.109)?
The problem is that every controller needs a disconnect, unless over 600V or unless there is a group of controllers.
Scenario: Cord and plug connected disposal. The cord and plug is the disconnect for the disposal, and the switch above the countertop is the controller (see controller] definition). The controller (switch) requires a disconnect within sight of the controller. In other words, you need a switch in front of the switch, to act as a disconnect for the switch!!!
What should the exception be?
Dwelling units?
Controllers with a marked "off" postition that switches all ungrounded conductors?
Controllers that meet the requirements to be used as a disconnect (430.109)?