440.22(c)
chris kennedy
Miami Fla.
Retired electrician
I have a situation where the EE speced a 200A safety switch fused at 110A for CU-1. The equipment arrives and it turns out CU-1 is actually two units that work in tandem. MOCP for each unit is 40A. While composing a RFI I sited 440.22(C). Although this is in chapter III of 440, upon reading 22(C) the highlighted areas below threw me:
Where maximum protective device ratings shown on a manufacturer?s overload relay table for use with a motor controller are less than the rating or setting selected in accordance with 440.22(A) and (B), the protective device rating shall not exceed the manufacturer?s values marked on the equipment.
Did I site the correct article?
Thanks
I'm seeing 'overcurrent' and 'overload' .
Here is the title of the section.
III. Branch-Circuit Short-Circuit and Ground-Fault Protection
Here is the article.
440.22(C) Protective Device Rating Not to Exceed the Manufacturer?s Values.
I'm confused by the first part of this sentence, why the talk of the overload relay chart?
To me, it means if the manufacturer has already gone through the trouble of listing the overload relays to be used with theire motor controller, then you cannot go above that number.
I'm not sizing overload relays, I'm sizing the fusible safety switch supplying the branch circuit conductors to the units.:-?
I agree that subsection is confusing. Every time I run into that one I mentally substitute "nameplate" for "overload relay table".