It is the voltage to ground that is the issue. 277v doesn't qualify as the voltage to ground is 480v. A straight 480 or 600v rated breaker does.

Either the delta is corner grounded (in which case he has 480 to ground) or it is ungrounded, in which case NEC says to use the line to line voltage instead (480 again), or he actually has a solidly grounded wye with the neutral missing, in which case the 480/277 would be OK.