We found the ground fault to be in one section of the plant; an area of about 4 acres. Within this area the feeders form a loop. It appears to have been configured in such a manner to allow for shutting down blocks of service while maintaining service to the rest of the area. Nothing the POCO doesn't do. However, some of the switch gear is circuit breakers and fused switches rather than simple switches. I understand the thinking for the blocks and for the protection but I don't think the circuit breakers or fuses would act any as automatic overload protection should the entire loop be energized, as it was. Keeping the loop from being fully energized is now a procedural issue after repairs are made.
The loop itself is not the cause of the ground fault. However, in the process of investigating the loop , we found the appearance of two separate faults on the same leg within the loop. In our inspection process we shut down one block where the overhead lines were ancient, had rotting crossarms and were in close proximity to a metal structure. We found no evidence of the lines having arched against the structure but the lines had enough slack to do so in a strong enough wind. We removed these lines altogether. We tested for faults before restoring power to the area and found none. We closed one switch and the fault returned. We opened this switch and closed the switch feeding the other end of the now former loop. A fault appeared on that end as well. We have been through the 480 side of the rest on the system in this area. There is one building fed underground through 60 year old pipe on the north end of the loop. That feeder is my prime suspect for the fault at this time. We'll are planning a shut down in that area in the coming weeks. If the building service isn't the problem then we have to start looking into the secondary side of everything in the area.
The other end is all newer work; underground in 3" conduits. We lines we removed were the first section of original lines where this new work comes out of the ground at one end of the loop. This newer work has three underground vaults along it's path. We are planning on a shutdown which will allow us to open the vaults and see what is going on in them. My first concern is that there are three line sets at the beginning but only one is currently in service. Two of the line sets are 3 wire 500 mcm with a bare ground wire that appears to be 3/0. The third set of 3 runs of 750 mcm, 15Kv cable with a 3/0 ground cable. The service starts on one set of the 500 mcm cable but ends up on the 15kV cable at the other end! I am assuming, which may be completely false, there is a good reason for this such as a cable went bad and someone switched it in a hasty repair. I have bandaids on turnicates on plaster casts. How do you eat an elephant? One bite at a time.
It looks like someone was thinking about bringing the primary all the way through the plant (this point is about as far as it gets from the substation) instead of having a substation at the POCO entry point. The work looks to be about 18 years old given the production dates on the wire and conduit. It is some of the best workmanship on property but there are zero records of who did it or why. It appears there was some work done about 10 years ago by the same company which contracts with the POCO for line work when the POCO crews are two busy.
I have convinced management to install a fourth wire on all of the 480 distribution and to replace the antique substation entirely. We are working with the POCO to supply us with a 480 volt temporary feed while the substation gear is removed, the PCB contaminated concrete floor is demoed, the structural brick repairs are completed, a new roof is installed, and the POCO brings in a new permanent underground primary service for us.
I did follow one contributor's recommendation and picked up a refurbished 3M fault detector.