It has been a long, long battle but we have located two major ground fault and one minor one, all on the same leg of the system. One fault was in an abandoned building. We simply cut power to the building and will deal with it if and when the facility is required in the future. Another fault was in an underground PVC conduit near a metal tower which rises some 60' above average terrain and appears to be ungrounded as it is sitting on concrete piers and has no ground rods. The final one is somewhere in an overhead line heading out to the far end of the property. With these faults cleared or simply off-line we have more normal voltage readings. Phase to phase is 480 volts anywhere on the system. On this 480 volt, ungrounded delta system we should be seeing 480 between each phase and ground. We are seeing 229, 226, and 220 to ground.
Any thoughts on this situation?
Thank you in advance.