I share Besoeker's concern.
_If_ the motor is designed to operate at 4160V and 60Hz, and is fed with a 480V to 4160V 60 Hz transformer...and then the VFD is being operated at 48Hz with an appropriately reduced output voltage, then the transformer is probably fine. Perhaps a suitable filter on the output of the VFD to remove some of the pwm noise would make sense, but I don't know that such is really necessary.
But this is exactly the sort of thing (voltage adjusted to match frequency) that one should not assume is actually what is going on.
-Jon
_If_ the motor is designed to operate at 4160V and 60Hz, and is fed with a 480V to 4160V 60 Hz transformer...and then the VFD is being operated at 48Hz with an appropriately reduced output voltage, then the transformer is probably fine. Perhaps a suitable filter on the output of the VFD to remove some of the pwm noise would make sense, but I don't know that such is really necessary.