IMHO the question of 'where can the grounded conductor serve as the fault current path' is a side discussion from the OP's issue.
The utility grounded conductor functions as part of the fault current path. The NEC splits this function to a separate EGC. This combined function is still permitted for the emergency disconnect. We can debate it endlessly.
The OP's issue is either the lack of proper bonding between grounded conductor and EGC, or proper ground fault detection.
Jonathan
The utility grounded conductor functions as part of the fault current path. The NEC splits this function to a separate EGC. This combined function is still permitted for the emergency disconnect. We can debate it endlessly.
The OP's issue is either the lack of proper bonding between grounded conductor and EGC, or proper ground fault detection.