Check out the e-mails below requesting some info and the response we got from the GC electrical coordinator. Just makes you wonder.
-----Original Message-----
From: Project Manager
To: Electrical Engineer
Dear Engineer,
Take a look at the responses to the above referenced RFI's. The architect and
design group are indicating all overhead doors were to have power?
Project Manager
-----Original Message-----
From: Electrical Engineer
To: Project Manager
Dear PM,
This is actually a kitchen equipment provider issue. If the doors were
not correctly specified and designed by design group as powered doors, then we
would not have shown power for these doors when coordinating with original
RFC documents.
If these doors are being changed to powered doors, please have
GC and equipment manufacturer provide you and us with the necessary
electrical information so that power can be added to these doors via
ASI.
Thanks,
Engineer
-----Original Message-----
From: Project Manager
To: GC
Dear GC,
We will need the voltage and load information for any overhead doors
that require power so that the engineer can issue ASI's.
Project Manager
-----Original Message----
From: GC Project Engineer
To: Sub Project Manager
Dear Sub PM/Engineer,
I just talked to equipment manufacturer's vendor and he said the overhead doors is
483 phase, 1/2 amp and you can use any voltage you want, just let him know.
Thanks,
GC Project Engineer
Any voltage in the 483 phase? No problem.
-----Original Message-----
From: Project Manager
To: Electrical Engineer
Dear Engineer,
Take a look at the responses to the above referenced RFI's. The architect and
design group are indicating all overhead doors were to have power?
Project Manager
-----Original Message-----
From: Electrical Engineer
To: Project Manager
Dear PM,
This is actually a kitchen equipment provider issue. If the doors were
not correctly specified and designed by design group as powered doors, then we
would not have shown power for these doors when coordinating with original
RFC documents.
If these doors are being changed to powered doors, please have
GC and equipment manufacturer provide you and us with the necessary
electrical information so that power can be added to these doors via
ASI.
Thanks,
Engineer
-----Original Message-----
From: Project Manager
To: GC
Dear GC,
We will need the voltage and load information for any overhead doors
that require power so that the engineer can issue ASI's.
Project Manager
-----Original Message----
From: GC Project Engineer
To: Sub Project Manager
Dear Sub PM/Engineer,
I just talked to equipment manufacturer's vendor and he said the overhead doors is
483 phase, 1/2 amp and you can use any voltage you want, just let him know.
Thanks,
GC Project Engineer
Any voltage in the 483 phase? No problem.