- Location
- Massachusetts
If he had 5-conductor SER, there'd be no need for a messenger wire to lash it to.
Actually there would be.
The code requires SER to be supported at intervals, the bare in it cannot be used as a messenger.
If he had 5-conductor SER, there'd be no need for a messenger wire to lash it to.
Where in the code?Actually there would be.
The code requires SER to be supported at intervals, the bare in it cannot be used as a messenger.
That AL bare conductor has a steel strand in the center for support - which is what ACSR is Aerial Cable Steel Reinforced.Some triplex has ACSR bare conductor, lots has AL bare conductor.
I continue to disagree with you on this issue. In my opinion triplex and quadplex are very clearly "identified" for the purpose and permitted by sixth list item in Table 396.10(A). Note that is the only list item in that table that does not have an NEC article reference.It is not a NRTL listed conductor type so we cant use it. If the manufacturers spent the money to have it listed we could use it.
Identified (as applied to equipment). Recognizable as suitable for the specific purpose, function, use, environment,
application, and so forth, where described in a particular Code requirement.
Where in the code?
338.10(B)(4)(b) Exterior Installations. In addition to the provisions
of this article, service-entrance cable used for feeders or
branch circuits, where installed as exterior wiring, shall be
installed in accordance with Part I of Article 225. The cable
shall be supported in accordance with 334.30. Type USE
cable installed as underground feeder and branch circuit
cable shall comply with Part II of Article 340.
334.30 Securing and Supporting. Nonmetallic-sheathed
cable shall be supported and secured by staples, cable ties,
straps, hangers, or similar fittings designed and installed so
as not to damage the cable, at intervals not exceeding 1.4 m
(41?2 ft) and within 300 mm (12 in.) of every outlet box,
junction box, cabinet, or fitting. Flat cables shall not be
stapled on edge.
Sections of cable protected from physical damage by raceway
shall not be required to be secured within the raceway.
You may be on something with this, first time I am aware of that bit of information anyway.I continue to disagree with you on this issue. In my opinion triplex and quadplex are very clearly "identified" for the purpose and permitted by sixth list item in Table 396.10(A). Note that is the only list item in that table that does not have an NEC article reference.
I see.IMO here ....
That AL bare conductor has a steel strand in the center for support - which is what ACSR is Aerial Cable Steel Reinforced.
Aluminum would not survive long without reinforcement - some short runs maybe are the exception. Otherwise the aluminum doesn't have the strength to support the load, and withstand additional load added by wind, snow and ice, etc.
Multiple conductors spaced evenly in free air, should probably have more impedance then if same conductors were multiplexed, or installed in close proximity in a raceway, but spacing them evenly does give you same impedance on each conductor because each one is subjected to same characteristics.
I continue to disagree with you on this issue. In my opinion triplex and quadplex are very clearly "identified" for the purpose and permitted by sixth list item in Table 396.10(A). Note that is the only list item in that table that does not have an NEC article reference.
Not all Triplex has ACSR. At lot of it doesn't. The spans for most service drops are not that long and AL is more than sufficient.
Did not look at your links, I do trust there is such a beast. You will not find it around here that I am aware of though. Lots of stuff with steel reinforcement does come down in both winter and summer storms we have here quite often. No steel would be even worse.
Though service drops designed to break away before pulling the service mast with them could have some benefits, just need to make sure the neutral is last conductor to break somehow and then you really have something people would be interested in.
I actually have not seen tripex with ACSR here. It probably depends on the POCO and the original engineer who wrote the first spec.
We have very few, if any, accidents that actually break the triplex, normally tree falls do rip the wiring / mast off the building.
I actually have not seen tripex with ACSR here. It probably depends on the POCO and the original engineer who wrote the first spec.
We have very few, if any, accidents that actually break the triplex, normally tree falls do rip the wiring / mast off the building.
One easy way to tell, cut it with your cable cutter that is for copper or aluminum only. If it leaves a scar in the cutting edge it is because there was a steel strand in it.:happyyes:I bet they are ASCR and you are mistaken.
I am just having a hard time imaging a single aluminum conductor supporting 2-4 other larger conductors over a 100'-150' span. Seems to me it would stretch and sag.
Of course in my area snow and ice loading is a yearly issue.