Have you ever seen single conductors approximately 2AWG or so grow to 4 inches diameter in ice covering? Even ACSR will sag pretty dramatically.
And your point is what here?:?
Have you ever seen single conductors approximately 2AWG or so grow to 4 inches diameter in ice covering? Even ACSR will sag pretty dramatically.
That it is pretty cool if you have seen itAnd your point is what here?:?
What about tray cable, lashed to a messenger? If it's sunlight resistant is there a problem, or are we back to the listsings issue (type TC is only listed for use in tray )
Nice idea! As long as you use multi listed tray cable with sunlight resistance. I've used some before that was also underground listed.
I don't think I have ever installed any tray cable that was not sunlight resistant and rated for direct burial.What about tray cable, lashed to a messenger? If it's sunlight resistant is there a problem, or are we back to the listsings issue (type TC is only listed for use in tray )
Nice idea! As long as you use multi listed tray cable with sunlight resistance. I've used some before that was also underground listed.
336.10(4) specifically permits TC to be used on a messenger wire as does Table 396.10(A).
I don't think I have ever installed any tray cable that was not sunlight resistant and rated for direct burial.
336.10(4) specifically permits TC to be used on a messenger wire as does Table 396.10(A).
I don't see this application as a permitted use as shown in 400.7, but I also don't see it as a prohibited use in 400.8If he's trying to get away from using a messenger wire, what about using an Article 400 [extra?] hard usage cord... would it need a messenger wire?
There was no span distance specified, but unless the span is very short, there will have to be supports between the two structures.Keep in mind that a steel messenger wire is desirable for long spans. I don't believe OP specified the span distance(s).
So he clearly cannot and can, respectively... :blink:I don't see this application as a permitted use as shown in 400.7, but I also don't see it as a prohibited use in 400.8
"Very short" is quite vague. There doesn't appear to be any way to determine the maximum distance between supports under the NEC.There was no span distance specified, but unless the span is very short, there will have to be supports between the two structures.
Underground is not a option. Im thinking muticonductor MC or service entrance cable. That transformer idea is quite creative. What a great forum.