At work I have noticed a feeder circuit that was recently installed. This feeder is protected by a 1600 amp breaker. The feeder consists of five parallel runs of MC Cable. On the outer jacket of each MC Cable is the following information:
Type MC, 3-conductor, 350 kcmil CU, XHHW-2, 3-AWG ground, Sun Resistant, 600V insulation.
2002 NEC 392.11(A) (3), in an open cable tray, for multiconductor cables, 2000V or less, with not more than three conductors per cable (ampacity to be determined from Table B310.3 in Annex B).
I believe the five parallel 350 kcmil XHHW-2 MC Cables are large enough for the 1600 amp feeder. What do you think?
How about the size of the ground (3AWG CU) in each MC Cable? Is this size ground large enough? Should the size be based on 250.122 which calls for 4/0 CU?
Please respond with your thoughts and questions. Thank you.