- Lockport, IL
- Retired Electrical Engineer
Bob (iwire) has asked me to read through this thread and offer an opinion. First, Bob, I thank you for your good opinion of my opinions, even though we have disagreed on several questions in the past.
I "sort of" disagree on this one as well, but not because I think anything you said was wrong. Rather, I think you didn't say enough. You had all the right ideas, but you didn't take them far enough. By the way, I also disagree with jcook980, and for the same reason.
This is not a subject I know well. I had to read through the various articles several times, before I saw the crux of the situation. Here's my take: You can, as jcook980 (and the engineer whose article he quoted) has said, use both the cable tray and the EGC within the MC cable as EGCs. In that, I am disagreeing with Bob. But I am also saying that the engineer's article did not tell the whole story.
The rest of the story is that if you chose to do use more than one of the fourteen elements listed as EGCs in 250.118, then each element you use must be fully rated for the job, as though no other element were there.
What I mean is that you cannot say, for example, that the EGC within the MC cable is rated for 25% of what an EGC needs to be (i.e., good for a 400 amp OCPD instead of 1600), and then say that the tray is good for 75% of what it needs to be (e.g., 1.125 sq. in. instead of 1.5), add the two, and say that you have 100% EGC coverage.
Specifically, as Bob correctly pointed out, 250.122(F) says that if you use the EGC in each parallel cable, then each EGC must be rated for the OCPD (i.e., for 1600), or you need to use GFP in the manner Bob described. Furthermore, as jcook980 correctly pointed out, 250.122(A) says "equipment grounding conductors of the wire type shall not be smaller than shown in Table 250-122. . . ." But what jcook980 is missing is that the facility MikeW has described is already using the wire type. Perhaps they will take credit for the tray as well. But if the wire type is used, then the wire type has to be "full-sized."
So what is my solution for the EGC problem? Presuming the cable tray is adequately sized, just cut the EGC wires in each MC cable short, and don't connect them. Use the tray, and nothing but the tray, as your EGC. Would that be "just plain silly," a waste of an available resource? I think not. The one thing you don't want to happen is for some later fool to think that he can disturb the tray sections and not worry about the EGC, because there is a "backup EGC" in place (i.e., the MC cable's EGC is a backup to the tray being an EGC). Don't give anyone that option. Deny him the use of the MC cable's EGC, and there will be no uncertainty of what is what.
And while we are at it, what is my solution for the ampacity problem? Not enough information was given. If the calculated load is under 1550, and if the breaker can be set to trip at 1550, then 5 sets of 350 MCM MC XHHW will suffice. If the load is between 1551 and 1600 amps, or if the load was not calculated, or if the breaker cannot be set to trip below 1600, then you need to hire an engineer, or you need to use more copper.