Because (NEMA) receptacle ratings are usually only 15, 20, 30, 50 and 60 amps.Why they're spec'ing a 50A receptacle instead of a 40A, I have no idea. But it is legal.
Because (NEMA) receptacle ratings are usually only 15, 20, 30, 50 and 60 amps.
Fact not yet in evidence.Ah. Well that explains it then. I'm just stupid.![]()
I don't understand why
this UL listed EV charger
can be specd using a 50 amp receptacle
which allows 42 amp flow and
only be required to be protected
by 40 amp fuse
Am I View attachment 13491my missing something?
Obviously!