frank melillo
Member
how meany 500mcm can go into 3.5 inch conduit
frank melillo said:how meany 500mcm can go into 3.5 inch conduit
frank melillo said:how meany 500mcm can go into 3.5 inch conduit
iwire said:Dennis with all the same size conductors how about using Annex C?
I guess we won't ask OP if theres a EGC involved.iwire said:Dennis with all the same size conductors how about using Annex C?
georgestolz said:saves papercuts.
chris kennedy said:And 90% of the time I have an EGC.
Bob, On all large jobs I double check ampacity, EGC sizing, conduit size and load calcs. I'll only find a couple of mistakes a year but a common one is under sized EGC. So correct that and now you find you have .003 in.2 left in a 200' run. More soap or next size up?iwire said:Once we get into larger circuits the plans usually have a conduit size indicated.
![]()
chris kennedy said:Bob, On all large jobs I double check ampacity, EGC sizing, conduit size and load calcs.
So correct that and now you find you have .003 in.2 left in a 200' run. More soap or next size up?