Go to table 4--- Conduit type-- If you are using PVC then the sq. in is 3.895 for 3 1/2" conduit.

Go to table 5 for 500 mcm thhn and the sq. in is .7073

now divide 3.895/.7073= 5.5

you can get 5 500 mcm THHN cables in 3.5 PVC
 
500mcm

sorry not to give all the info i had three phones in ear when asking.
thank to all for you help.
this question forum is great
 
You know I always hated using Annex C because it took so long to find the correct page. I just realized that the first page (which I must of missed all these years) has an index--- much easier.
 
georgestolz said:
saves papercuts.

How's this for a papercut?
Stitches and tape to hold end of thumb on:

attachment.php
 
chris kennedy said:
And 90% of the time I have an EGC.

I usually carry an EGC as well.

That said I bet 90% of the runs we have to figure have the same size EGC as the circuit conductors.

Once we get into larger circuits the plans usually have a conduit size indicated.

I agree it is not a 'hard calculation' but a table is faster. :)
 
iwire said:
Once we get into larger circuits the plans usually have a conduit size indicated.

:)
Bob, On all large jobs I double check ampacity, EGC sizing, conduit size and load calcs. I'll only find a couple of mistakes a year but a common one is under sized EGC. So correct that and now you find you have .003 in.2 left in a 200' run. More soap or next size up?
 
chris kennedy said:
Bob, On all large jobs I double check ampacity, EGC sizing, conduit size and load calcs.

I will never say always.:D

Ampacity: I will check if something seems out of whack.

EGC: I will check if something seems out of whack.

Conduit size: I will check if something seems out of whack.

Load Calcs: Never, that is definitely the engineers issue as far as I am concerned.

How can I 'check' load calcs? I will have no idea the method they used to arrive at their answers.

So correct that and now you find you have .003 in.2 left in a 200' run. More soap or next size up?

I have no problem using a code minimum size conduit in some instances.

The size of the conduit does not change the pulling tension assuming the conduit is at least code minimum.

I had a 1,600 amp feeder to run specified as five sets of 500 kcmil XHHW + grd in five - 4" RMC. I did the math and got approved to run five sets of 3" EMT instead. The run had to go above an existing crowded suspended ceiling, I needed it as compact as I could get away with.

and yes.....we used a lot of soap. :D

On the other hand PVC underground we will usually go bigger than needed.
 